June 6th, 2013 10:32 AM #62
No need to buy a phase converter.. Iba ito sa iniisip mo.
Bro.- 3phase - 3 sinusoidal waves iyan na 120deg off phase sa isa't isa,- kaya walang time na zero ang voltage - pang machine application.
Bro.,- Puwedeng line to line or line to neutral(kung WYE configuration) ang kunin mong linya (isa ito sa 3 sinusoidal wave)... Pero,- tama ba ang voltage nito sa iyong requirement? A multimeter set to VAC should be able to give you the effective voltage level... However, the frequency should be spec'ed on your genset.
Typically line to line voltage is 1.73 x line to neutral voltage. (1.73 is square root of 3)
I assume may ground iyan... i measure mo rin ang line to ground voltage.
Else, kailangan mo ng step up or step down transformer,- whatever is appropriate.
19.4K:tomato:Last edited by CVT; June 6th, 2013 at 10:42 AM.
-
-
June 6th, 2013 10:51 AM #64
Bro., simple lang (di ba ME ka ng mahal nating Berde?)...
1. Get a multimeter and set it to VAC (voltage - AC)
2. 3-phase iyan so tatlo ang ports or "lines"
3. Connect your multimeter probes in 2 of those terminals
4. It should read 220V for you to able to use it in your house.
5. If 220V - then connect those two ports you just measured to your house electrical line. You should be okay
6. If not - say 400V - you need a stepdown transformer to bring it down to 220V - take note of the power requirement of your house - 5KVA/W for example
7. If not - say 110V - you need a step up transformer to bring it up to 220V - take note of the power requirement of your house - 5KVA/W for example
8. Frequency - read it from the manual or the plate on the genset - should be 60Hz. If not you need a frequency or phase converter.
19.4K:tomato:
-
June 6th, 2013 10:59 AM #65
Di ba nagkaka uneven load sa genset if 2 terminals/lines lang ang gagamitin ko?
240V ang voltage ng genset.
And if 2 terminals/lines lang gamitin ko, tama ba na hindi na full capacity ng genset ang magagamit ko?Signature
-
June 6th, 2013 11:03 AM #66
Uneven loading should be the least of your worries bro.
Actually, ginagawa iyang load balancing ng power distribution companies....
Yes,- hindi full capacity ng genset dahil iyong dalawang phases,- walang load,- wasted energy pero minimum lang dahil nga walang load.... Your new capacity is full capacity of genset divided by 1.73.
Ano ang full power capacity ng 3-phase genset mo?
Important na 60Hz iyan,- else delikadong gamitin ang aircon, ref at ibang motors sa bahay.....
19.4K:tomato:Last edited by CVT; June 6th, 2013 at 11:07 AM.
-
June 6th, 2013 11:04 AM #67
45kva.
Sabi kasi ng electrician masisira daw dynamo if uneven ang load.Signature
-
June 6th, 2013 11:22 AM #68
-
June 6th, 2013 11:26 AM #69
So if my genset is 45KVA and I'll just use one phase, what's the equivalent capacity that I can utilize from the genset?
Right now, my genset supplies the following:
1 phase to my office
1 phase to our dirty kitchen/dining/maid's quarters/workers' quarters
1 phase to the house.
Lilipat ko na kasi office ko so mawawalan\ ng load sa office. Mababawasan din yung load sa isa kasi lilipat din workers' quarters.Signature
-